Another Battery Fire in AT&T's Network

Posted by CowboyNeal on Sat Aug 25, 2007 08:13 AM
from the hot-stuff dept.
An anonymous reader writes "AT&T has disclosed another fire started by one of the 17,000 Avestor batteries in its broadband network. The first fire caused a violent explosion in suburban Houston. This second incident occurred just 20 miles away."
+ -
story

Related Stories

[+] Hardware: Batteries the Focus of AT&T Investigation 80 comments
An anonymous reader writes "AT&T is focusing on the batteries supplied by Avestor as the cause of its 2006 equipment explosion in a suburban Houston neighborhood. The carrier says it has 17,000 of those same batteries still in its network. Some photos of the equipment that was shredded in the blast are also available."
[+] Hardware: AT&T To Replace 17,000 Batteries 71 comments
An anonymous reader writes "After four fires in two years — see earlier Slashdot discussions for background — AT&T is going against its own independent lab findings and declaring that the Avestor batteries powering its U-verse network aren't safe and need to be replaced. This is the network that SBC was building out prior to acquiring AT&T. Following the latest broadband equipment cabinet explosion in Wisconsin, the carrier says it will swap out 17,000 batteries deployed in several states across its network."
This discussion has been archived. No new comments can be posted.
The Fine Print: The following comments are owned by whoever posted them. We are not responsible for them in any way.
 Full
 Abbreviated
 Hidden
More
Loading... please wait.
  • I can't imagine if one of these went off in say, northern El Cajon California. There would probably be a huge brush fire at least, all it takes is one spark to hit that bone-dry foliage. Does anyone know if these batteries are installed all over or just in TX?
  • Wow (Score:3, Interesting)

    by Durrok (912509) <calltechsucks&gmail,com> on Saturday August 25 2007, @08:23AM (#20353259) Homepage Journal
    From TFA: "Outside of these two incidents, there have been no similar incidents involving these batteries," AT&T's spokesman writes via email.

    Anyone else read ".... YET" in that sentence. I'm hoping they are doing further testing in whatever conditions these batteries were in that made them explode. TFA did not mention anything but then again it is light reading.
    • "Anyone else read ".... YET" in that sentence"

      Yes, I did, take the quote from the bigwig:

      "the battery design was sound, as were the safety features," and concluded that "the risk of hazardous failures with this battery is as low, if not lower, than the risk with alternative batteries, which are used by other telecommunications and cable companies in similar applications."

      IF the battery design was sound, why did 2 of them start fires?

      • Just wait for it, the word of the decade (terrorism) is going to come up in just a matter of time...you watch.
        • Re: (Score:2, Informative)

          Don't be silly - nobody would make an unreasonable conclusion that this was a terrorist attack - after all, everybody knows that Al Qaeda planned this attack so carefully that nobody would notice.
      • Well it's hard to say, many electric devices can start fires/malfunction if treated incorrectly. Were they exposed to water? Intense heat? Corrosive chemicals? If the situation for those two batteries was far beyond the norm of use then it's not necessary to replace all the batteries, just to post notice or possibly move the boxes to a better location (Which would be a lot more work then just replacing the batteries I'm sure). I'm not saying they should go recall all of these immediately but I really hope t
        • Maybe I am just pessimistic, but the fact that the bigwigs do not explain the circumstances behind the fires makes me unsettled. Sure, there could be a natural explanation (Summer heat + some unfortunate other circumstance) or misuse, but what troubles me is that the bigwig said the batteries were safe without a full investigation.

          Now maybe this is for legal reasons, but at the very least they should explain why this happened and how to prevent it from happening again. Or if the batteries are indeed safe,
        • Re:Wow (Score:5, Insightful)

          by grumling (94709) on Saturday August 25 2007, @09:33AM (#20353565) Homepage
          If they were within 20 miles of each other, I'd look at the other ones nearby and find out who installed them. Maybe the contractor needs a little more training, maybe they got a bad batch of batteries.

          It is likely they were installed by the same group of people (person?), and if they (he) didn't know what he was doing, it may very well happen again. It is also likely the batteries were all part of the same batch.
          • If they were within 20 miles of each other, I'd look at the other ones nearby and find out who installed them. Maybe the contractor needs a little more training, maybe they got a bad batch of batteries.


            It also should be noted that (depending on your source) Houston, TX is the second hottest city in the United States, when looking at daily mean.
            • by Anonymous Coward

              Houston, TX is the second hottest city in the United States, when looking at daily mean.
              What about when you look at women?
          • I would suspect that heat has something to do with the failures. Houston is pretty hot.
          • It is also likely the batteries were all part of the same batch.

            Yes, I understand that Avestor made some twenty thousand of the things before going bankrupt.
        • Were they exposed to intense heat?
          Well, they were in Houston after all.
        • Were these batteries exposed to water? Maybe--there has been a lot of rain in the Southern Plains this year. Tropical Storm Erin just passed through, but there was enough rain before that.
          Were they exposed to heat? Yes. It's been a very hot summer this year, or at least this month, in the Southern Plains when it hasn't been raining. Nineties or 100s(Fahrenheit).
          Corrosive chemicals? Probably not. But these batteries are li-poly! They can explode without help from other chemicals.
      • I think it definitely needs to be investigated. Two batteries in 17,000 randomly failing is one thing (and probably not a bad rate, assuming none of the other 17,000 only failed), but starting fires is another issue altogether.
    • You could try cracking a joke that had something to do with the article, or at the very least to a comment.

      That post was a waste of all our time, and a moderators mod points, and your Karma.
    • FWIW- I see the joke you were trying to make. Just imperfect delivery I guess. Mods can be very jumpy with the MS topic
    • I was at Sprint PCS a few years ago. I remember hearing about the power failure in Ft. Worth, TX. The batteries drained down in the UPS, so the power generator was started. It caught fire and people were air lifted to hospital. When I'm in the Ft. Worth area I go to visit that data center and just think about the horror Sprint, EMC, Sun and Veritas people suffered one night a few years ago.
    • Re: (Score:3, Informative)

      You have to distinguish between two types of lead-acid batteries and then the whole thing is not that optimal anymore.

      With wet-cell lead-acid batteries [wikipedia.org] you'll get evaporation and resulting loss of capacity. Beside that you have a precipitation of lead(II) sulfate that can ultimately kill your battery.

      With maintenance-free (sealed) batteries like Valve Regulated Lead Acid batteries you do not get these problems but you could get thermal runaway [hanford.gov] and they do explode. Gel-batteries [wikipedia.org] are less inclined to expl

      • Re: (Score:1, Informative)

        by Anonymous Coward
        The lead-acid batteries I'm familiar with are large, have clear cases, lots of room below the plates and probably quite wide spacing between the plates. Banks of them fill large rooms. They are one of the reasons that POTS (plain old telephone service) works even when the power goes out everywhere else. They are also the reason why air traffic control towers continue to work even if the diesel generator doesn't start quickly. All of the problems you mention don't affect them.

        Having said the above, even
      • On the other hand lithium metal polymer are said to "have service lives as long as 10 years, under ambient temperatures from -40C to +65C."

        Funny thing is, I've got here plenty of manufacturer data sheets claiming pretty much the same thing for SLA / VRLA batteries.

        In practice, for ambient temps between 15C & 40C, service life seemed to be ~ 3 years max. And not much, if any, better in a regulated 25C ~30C environment.

        OTOH, I remember these being used to replace batteries of flooded lead-acid cells, su

  • Of course, when the hottest thing you have to offer your customers is an actual fire it's not quite the same.
  • by phoenixwade (997892) on Saturday August 25 2007, @08:42AM (#20353357) Homepage

    The two batteries referred to were housed in two different VRAD cabinets, 20 miles apart, in the same city within a few months of each other. But, the carrier says, apart from those two batteries, all else is well. In its statement, published earlier today, AT&T said "the battery design was sound, as were the safety features," and concluded that "the risk of hazardous failures with this battery is as low, if not lower, than the risk with alternative batteries, which are used by other telecommunications and cable companies in similar applications."
    Really? the ubiquitous SLA has the same track record? What a crock 'o poopie. Another one of those "I think I'll pull statistics out of my ass and spout them off" moments....

    What I can't figure out is why they aren't using SLA's in those cabinets in the first place. They are, by far, the most common battery in use in almost every application. The advantage is that SLA's are safe, predictable and cheap. The disadvantages are volume and weight, but in a stationary cabinet that shouldn't make a difference.
  • by LWolenczak (10527) <lw@lwolenczak.net> on Saturday August 25 2007, @08:42AM (#20353359) Homepage Journal
    It really doesn't surprise me. Sealed cell VRLA Battery + High Temperatures (Summer) + Hydrogen creation inside battery from the Water/Acid mix + brown out causing battery to be utilized = practical bomb. I had one cook off in a generator this week. One of my data center generators went to start up for its weekly exercise this week and it never started, but one of the batteries exploded. It didn't lead to a fire, but I'm sure it would have if it was in a more confined space.
    • Sealed cell VRLA Battery

      Er, read the article (again). They're Lithium Polymer (LiPo) batteries. Remember those exploding Lithium-Ion laptop batteries a couple of months ago? These are even more dangerous. This [youtube.com] should give you an idea... and that's a small one.
      • Whoops, I have been corrected. I would have assumed VRLA given thats the standard, at least inside central offices and DC powered data centers. If its a lithium battery, then they are just plum overcharging it.
        • FWIW anyway, there is a similar risk with wet cell batteries, but they are not small, and they are typically monitored very closely. Most rooms I've seen wet cells in have hydrogen sensors and ventilation.
  • And you might end up with a little problem.

    http://www.askthepilot.com/upsfire.html [askthepilot.com]

    Story that explains the picture:
    http://www.salon.com/tech/col/smith/2006/09/22/ask thepilot202/print.html [salon.com]

    Granted, Smith is a pilot, not an engineer, but he gives a somewhat good explanation of thermal runaway.
  • Verizon's FIOS is in my area. I won't subscribe because I hate Verizon with a passion, but I've got photos of their cabinets and they look nothing like at&t's cabinets.

    http://www.flickr.com/photos/kd1s/553921527/in/set -72157594534810671/ [flickr.com]
  • Aventes has filed for bankruptcy:

    http://www.greencarcongress.com/2006/11/avestor_sh uts_d.html [greencarcongress.com]

    Avestor, the Canadian developer of Lithium-Metal-Polymer (LMP) battery technology, is shutting down. The company filed with the Office of the Superintendent of Bankruptcy in Montréal with a view to making a Proposal to its creditors on 31 October.

    In August, the company had produced and shipped its 20,000th battery. At that time, Avestor said it had signed multimillion dollar, multiyear contracts with ma

  • yep

    http://www.greencarcongress.com/2006/11/avestor_sh uts_d.html [greencarcongress.com]

    our telecom outfit had ship issue after ship issue and RMA issue after RMA issue, before we finally got a tech advisory that the vendor was shyt outta luck, and use sealed lead-acid for field replacements.

    which will probably improve reliability immensely.

    if you have any, seriously consider replacing them with non-incendiary technology.
  • Wake up take your head out of your ass and buy Flywheel batteries. Caterpillar sells them for god sakes. No maintenance, rapid charge and discharge, and so reliable that you can send them into space at 10,000 USD per pound to orbit.